perspicacious:
I will post further if I can find the information in my files that are now in the loft.
Thank you Mike. I'm sure others will find this "derating" of interest!
Regards
BOD
Bod
Found it!! Not sure if this applies directly to your situation, but, this may go some way to helping you.
Quote from Wylex NM CU Installation Instructions - have scanned & pasted below:
Ambient Temperature Considerations
The NH Range of MCB's are calibrated to meet the 30°C Ref Calibration Temperature
requirements of BSEN 60898.
At other temperatures the following rating factors should be used:
At 60°C 0.9 At 20°C 1.0 At 0°C 1.1
Adjacent thermal-magnetic MCBs should not be continuously loaded or approaching
their nominal rated currents when mounted in enclosures. It is good I!
engineering practice to apply generous derating factors or make provision for adequate
free air between· devices. In these situations, and in common with other; manufacturers, we
recommend a 60% diversity factor is applied to the MCB nominal rated current where it is
intended to load the MCB' s continuously (in excess of 1 hour)
Before fitting the front cover, check the tightness of all connections,
Hope this helps
Regards
Mike
perspicacious:
I will post further if I can find the information in my files that are now in the loft.
Thank you Mike. I'm sure others will find this "derating" of interest!
Regards
BOD
Bod
Found it!! Not sure if this applies directly to your situation, but, this may go some way to helping you.
Quote from Wylex NM CU Installation Instructions - have scanned & pasted below:
Ambient Temperature Considerations
The NH Range of MCB's are calibrated to meet the 30°C Ref Calibration Temperature
requirements of BSEN 60898.
At other temperatures the following rating factors should be used:
At 60°C 0.9 At 20°C 1.0 At 0°C 1.1
Adjacent thermal-magnetic MCBs should not be continuously loaded or approaching
their nominal rated currents when mounted in enclosures. It is good I!
engineering practice to apply generous derating factors or make provision for adequate
free air between· devices. In these situations, and in common with other; manufacturers, we
recommend a 60% diversity factor is applied to the MCB nominal rated current where it is
intended to load the MCB' s continuously (in excess of 1 hour)
Before fitting the front cover, check the tightness of all connections,
Hope this helps
Regards
Mike