perspicacious:
....we recommend a 60% diversity factor is applied to the MCB nominal rated current where it is
intended to load the MCB' s continuously (in excess of 1 hour).
...
Hmm, so a EICR carried out on my dwelling with a 16 A circuit-breaker on my 3 kW immersion heater in a 210 litre cylinder would result in what code? ...
Well reading the rest of the advice, it only applies to close packed breakers, so no code if the breakers on either side were lightly loaded, or its suggests you should fit a 20A one if they are.
Perhaps they think we should fit 40A breakers to 32A rings to avoid stressing the breakers. I'd disagree.
I suggest that like the total demand diversity calculations themselves, where we see breakers totally 200-300A on a 100A company fuse with no issues , this is so much cobblers.
regards
Mike.
perspicacious:
....we recommend a 60% diversity factor is applied to the MCB nominal rated current where it is
intended to load the MCB' s continuously (in excess of 1 hour).
...
Hmm, so a EICR carried out on my dwelling with a 16 A circuit-breaker on my 3 kW immersion heater in a 210 litre cylinder would result in what code? ...
Well reading the rest of the advice, it only applies to close packed breakers, so no code if the breakers on either side were lightly loaded, or its suggests you should fit a 20A one if they are.
Perhaps they think we should fit 40A breakers to 32A rings to avoid stressing the breakers. I'd disagree.
I suggest that like the total demand diversity calculations themselves, where we see breakers totally 200-300A on a 100A company fuse with no issues , this is so much cobblers.
regards
Mike.
We're about to take you to the IET registration website. Don't worry though, you'll be sent straight back to the community after completing the registration.
Continue to the IET registration site