This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

circuit-breaker allegedly "getting more sensitive"

Former Community Member
Former Community Member
OK, usual caravan park issues with more pitches than incoming supply, so client has acknowledged this by installing 10 A circuit-breakers for each 16 A outlet. With 24 pitches on a presumed 80 A single-phase cut-out, he has got away with it..... so far, but he doesn't close for winter....


He has a few regulars that complain about the 10 A circuit-breaker being too sensitive so client believes them and has fitted new 10 A circuit-breakers ready for this weekend.


Considering that a 10 A circuit-breaker will run at 11.3 A continuously and 16 A for about 10 minutes, I'm more inclined to think that the "shed puller's" use of the 2 kW built in heater, 2 kW supplementary fan heater, fridge and domestic 3 kW kettle plus entertainment equipment are more likely....


But, has anyone carried out any tests on circuit-breakers to prove/disprove the alleged reduced rating? Or links to any such reports?


Regards


BOD
Parents
  • I have been paid to stand with a stop watch and a thermometer to find out how long it takes to fill a walk-in bath with water at 38 degrees and to what depth it can be filled.


    I can assure you you need a big cylinder with the water in it pushing 60 degrees, so the thermostatic mixer can blend it down with cold water. Most cylinders will fill a walk-in to about an inch and a half above the seat, which is not enough.
Reply
  • I have been paid to stand with a stop watch and a thermometer to find out how long it takes to fill a walk-in bath with water at 38 degrees and to what depth it can be filled.


    I can assure you you need a big cylinder with the water in it pushing 60 degrees, so the thermostatic mixer can blend it down with cold water. Most cylinders will fill a walk-in to about an inch and a half above the seat, which is not enough.
Children
No Data