Cable Lugs

The project specification says, "All compression connectors for 10mm2 and larger conductors shall have a manufacturer's reference compression die number and conductor size printed or stamped on the connector".


If the marking requirement is not complied by lug vendors on the pad/tongue of the lugs, the same can be pressed into the lugs during crimping, using appropriate dies. Is this acceptable?


 I say this because the pressed marking on the crimping part would be compared with the factory markings on the pad/tongue of the lugs for verification.

Even if the factory markings are not provided, the pressed marking on the crimping part would be verified with the catalogues /datasheet of the lugs.

Parents
  • I have not seen a manufacturers die number on a crimp or die only the size only the impressed CSA and the makers name on the crimp and, as Chris says, the 95/12 type marking for the CSA and bolt size.


    Is this some sort of very specialist installation in something like a nuclear plant? Or is it a generic cut and paste spec? If it is the latter go back and question it and ask why explaining that you will be using manufacturers lugs (whoever) and the CSA will be impressed on to the lug by the die.
Reply
  • I have not seen a manufacturers die number on a crimp or die only the size only the impressed CSA and the makers name on the crimp and, as Chris says, the 95/12 type marking for the CSA and bolt size.


    Is this some sort of very specialist installation in something like a nuclear plant? Or is it a generic cut and paste spec? If it is the latter go back and question it and ask why explaining that you will be using manufacturers lugs (whoever) and the CSA will be impressed on to the lug by the die.