New EICR "unsatisfactory" - complete rewire required?!?

Former Community Member
Former Community Member
The lighting circuit has no CPC (earth), this is not uncommon in older houses. For that reason all light fittings are Class 2 i.e. plastic with no metal, and there is a clause in the tenancy agreement which forbids tampering with the light fittings (this is a house we own and rent out).


Previous EICRs did not even mention the lighting circuit because of the Class 2 fittings. I have just got a new EICR with an observation "lighting circuits have little or no earth" and classification code C1 ("Danger present, risk of injury, immediate remedial action required"). The overall assessment says "Unsatisfactory" with the comment "Needs updating to current regs". This can only be fixed by a complete rewire of the whole lighting circuit.


This is pointless, there are no earth connections in the plastic fittings.


Any thoughts? Many thanks.
Parents
  • I see no reason to rewire the lighting completely if everything is class 2, and the wiring is otherwise satisfactory. It is not compliant with BS7671 (18th) but is not in any way "Dangerous".A competent electrician would simply not fir a class 1 light fitting, or would add an Earth wire to that point. I assume that all the switches etc are also plastic and everything is mechanically protected correctly? I would code this as a C3 (improvement suggested) and so the install would be satisfactory.
Reply
  • I see no reason to rewire the lighting completely if everything is class 2, and the wiring is otherwise satisfactory. It is not compliant with BS7671 (18th) but is not in any way "Dangerous".A competent electrician would simply not fir a class 1 light fitting, or would add an Earth wire to that point. I assume that all the switches etc are also plastic and everything is mechanically protected correctly? I would code this as a C3 (improvement suggested) and so the install would be satisfactory.