This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

New EICR "unsatisfactory" - complete rewire required?!?

Former Community Member
Former Community Member
The lighting circuit has no CPC (earth), this is not uncommon in older houses. For that reason all light fittings are Class 2 i.e. plastic with no metal, and there is a clause in the tenancy agreement which forbids tampering with the light fittings (this is a house we own and rent out).


Previous EICRs did not even mention the lighting circuit because of the Class 2 fittings. I have just got a new EICR with an observation "lighting circuits have little or no earth" and classification code C1 ("Danger present, risk of injury, immediate remedial action required"). The overall assessment says "Unsatisfactory" with the comment "Needs updating to current regs". This can only be fixed by a complete rewire of the whole lighting circuit.


This is pointless, there are no earth connections in the plastic fittings.


Any thoughts? Many thanks.
Parents
  • I am glad that we all agree on this one. This is again an attempt at extortion, or the inspector is not competent and should be reported to his certifying body. There is far too much of this kind of thing going on, see another thread here.
Reply
  • I am glad that we all agree on this one. This is again an attempt at extortion, or the inspector is not competent and should be reported to his certifying body. There is far too much of this kind of thing going on, see another thread here.
Children
No Data