New EICR "unsatisfactory" - complete rewire required?!?

Former Community Member
Former Community Member
The lighting circuit has no CPC (earth), this is not uncommon in older houses. For that reason all light fittings are Class 2 i.e. plastic with no metal, and there is a clause in the tenancy agreement which forbids tampering with the light fittings (this is a house we own and rent out).


Previous EICRs did not even mention the lighting circuit because of the Class 2 fittings. I have just got a new EICR with an observation "lighting circuits have little or no earth" and classification code C1 ("Danger present, risk of injury, immediate remedial action required"). The overall assessment says "Unsatisfactory" with the comment "Needs updating to current regs". This can only be fixed by a complete rewire of the whole lighting circuit.


This is pointless, there are no earth connections in the plastic fittings.


Any thoughts? Many thanks.
Parents
  • Former Community Member
    0 Former Community Member
    John Peckham:

    JPC


    "Tenants should not be touching electrical installations, Class 1 or otherwise. If they do, you really cannot prevent them harming themselves"


    So clearly you cannot use double insulation as a method of protection as the installation is not under effective supervision?



    Nothing is effective as a method of protection if tenants start fiddling with electrical installations. You said as much yourself really, in your post: "even though the circuits have a CPC I find un-earthed light fittings and dimmer switches ". Those fiddled-with metal Class 1 light fittings and dimmer switches are even more dangerous than a Class 2 fixture.


Reply
  • Former Community Member
    0 Former Community Member
    John Peckham:

    JPC


    "Tenants should not be touching electrical installations, Class 1 or otherwise. If they do, you really cannot prevent them harming themselves"


    So clearly you cannot use double insulation as a method of protection as the installation is not under effective supervision?



    Nothing is effective as a method of protection if tenants start fiddling with electrical installations. You said as much yourself really, in your post: "even though the circuits have a CPC I find un-earthed light fittings and dimmer switches ". Those fiddled-with metal Class 1 light fittings and dimmer switches are even more dangerous than a Class 2 fixture.