New EICR "unsatisfactory" - complete rewire required?!?

Former Community Member
Former Community Member
The lighting circuit has no CPC (earth), this is not uncommon in older houses. For that reason all light fittings are Class 2 i.e. plastic with no metal, and there is a clause in the tenancy agreement which forbids tampering with the light fittings (this is a house we own and rent out).


Previous EICRs did not even mention the lighting circuit because of the Class 2 fittings. I have just got a new EICR with an observation "lighting circuits have little or no earth" and classification code C1 ("Danger present, risk of injury, immediate remedial action required"). The overall assessment says "Unsatisfactory" with the comment "Needs updating to current regs". This can only be fixed by a complete rewire of the whole lighting circuit.


This is pointless, there are no earth connections in the plastic fittings.


Any thoughts? Many thanks.
Parents
  • Former Community Member
    0 Former Community Member
    Chris Pearson:

    So the least bad solution might be to rewire the circuit.


    The tenant does NOT want that. I have talked to her and she is happy that the electrics are safe (it passed EICR five years ago and nothing has changed). She works from home and has children. Re-wiring would be very disruptive and very dusty because wires are buried in the wall and not conduited. The house is full of furniture which would have to be removed. It would be a nightmare for her.


    If the house was between tenants and empty I might agree.


     


Reply
  • Former Community Member
    0 Former Community Member
    Chris Pearson:

    So the least bad solution might be to rewire the circuit.


    The tenant does NOT want that. I have talked to her and she is happy that the electrics are safe (it passed EICR five years ago and nothing has changed). She works from home and has children. Re-wiring would be very disruptive and very dusty because wires are buried in the wall and not conduited. The house is full of furniture which would have to be removed. It would be a nightmare for her.


    If the house was between tenants and empty I might agree.


     