John Peckham:
JPC
"Tenants should not be touching electrical installations, Class 1 or otherwise. If they do, you really cannot prevent them harming themselves"
So clearly you cannot use double insulation as a method of protection as the installation is not under effective supervision?
John, I also note 411.3.1.1 - CPC required at every point in wiring with the exception of the two-core between a ceiling rose and a pendant lamp holder.
Would your code be influenced by the presence of RCD protection? (I realize that it wouldn't stop a class I light fitting being live until somebody provided a pathway to Earth.)
John Peckham:
JPC
"Tenants should not be touching electrical installations, Class 1 or otherwise. If they do, you really cannot prevent them harming themselves"
So clearly you cannot use double insulation as a method of protection as the installation is not under effective supervision?
John, I also note 411.3.1.1 - CPC required at every point in wiring with the exception of the two-core between a ceiling rose and a pendant lamp holder.
Would your code be influenced by the presence of RCD protection? (I realize that it wouldn't stop a class I light fitting being live until somebody provided a pathway to Earth.)