New EICR "unsatisfactory" - complete rewire required?!?

Former Community Member
Former Community Member
The lighting circuit has no CPC (earth), this is not uncommon in older houses. For that reason all light fittings are Class 2 i.e. plastic with no metal, and there is a clause in the tenancy agreement which forbids tampering with the light fittings (this is a house we own and rent out).


Previous EICRs did not even mention the lighting circuit because of the Class 2 fittings. I have just got a new EICR with an observation "lighting circuits have little or no earth" and classification code C1 ("Danger present, risk of injury, immediate remedial action required"). The overall assessment says "Unsatisfactory" with the comment "Needs updating to current regs". This can only be fixed by a complete rewire of the whole lighting circuit.


This is pointless, there are no earth connections in the plastic fittings.


Any thoughts? Many thanks.
Parents
  • I don't know why you want further explanation Sparkingchip. A previous EICR may have given this as a code C3, which is simply a recommendation. You seem to think that YOUR opinion is the only one allowed but it is not. How is it in any way unsafe (particularly as the circuit is RCD protected)? It would be interesting to hear. A C3 does not require correction to the latest regulations.
Reply
  • I don't know why you want further explanation Sparkingchip. A previous EICR may have given this as a code C3, which is simply a recommendation. You seem to think that YOUR opinion is the only one allowed but it is not. How is it in any way unsafe (particularly as the circuit is RCD protected)? It would be interesting to hear. A C3 does not require correction to the latest regulations.