New EICR "unsatisfactory" - complete rewire required?!?

Former Community Member
Former Community Member
The lighting circuit has no CPC (earth), this is not uncommon in older houses. For that reason all light fittings are Class 2 i.e. plastic with no metal, and there is a clause in the tenancy agreement which forbids tampering with the light fittings (this is a house we own and rent out).


Previous EICRs did not even mention the lighting circuit because of the Class 2 fittings. I have just got a new EICR with an observation "lighting circuits have little or no earth" and classification code C1 ("Danger present, risk of injury, immediate remedial action required"). The overall assessment says "Unsatisfactory" with the comment "Needs updating to current regs". This can only be fixed by a complete rewire of the whole lighting circuit.


This is pointless, there are no earth connections in the plastic fittings.


Any thoughts? Many thanks.
Parents
  • Former Community Member
    0 Former Community Member
    Sparkingchip:

    However if anything goes wrong the question will be asked why you let the tenant move in when you knew it did not have a CPC.


    Assuming the previous EICR recommended improvement why didn’t you act on the report will be the question.


    Your reply that you still don’t consider it needs improvement may require dome explanation.


    I DID act on the report. The previous EICR said there was no CPC in the lighting circuit, so I changed all light fittings to Class 2.


Reply
  • Former Community Member
    0 Former Community Member
    Sparkingchip:

    However if anything goes wrong the question will be asked why you let the tenant move in when you knew it did not have a CPC.


    Assuming the previous EICR recommended improvement why didn’t you act on the report will be the question.


    Your reply that you still don’t consider it needs improvement may require dome explanation.


    I DID act on the report. The previous EICR said there was no CPC in the lighting circuit, so I changed all light fittings to Class 2.