New EICR "unsatisfactory" - complete rewire required?!?

Former Community Member
Former Community Member
The lighting circuit has no CPC (earth), this is not uncommon in older houses. For that reason all light fittings are Class 2 i.e. plastic with no metal, and there is a clause in the tenancy agreement which forbids tampering with the light fittings (this is a house we own and rent out).


Previous EICRs did not even mention the lighting circuit because of the Class 2 fittings. I have just got a new EICR with an observation "lighting circuits have little or no earth" and classification code C1 ("Danger present, risk of injury, immediate remedial action required"). The overall assessment says "Unsatisfactory" with the comment "Needs updating to current regs". This can only be fixed by a complete rewire of the whole lighting circuit.


This is pointless, there are no earth connections in the plastic fittings.


Any thoughts? Many thanks.
Parents
  • Twisting words. 

     Wiring , to a previous ed, (14th) is "not necessarily unsafe" This wiring is not unsafe. 

    It is unreasonable to rewire this lighting circuit. 

    There are millions of buildings wired to previous eds, far outweighing any wired to the 18thed. more probably to the 14thed than any other. There are many with a water main/rod earth with an excellent ELI. They are safe for continued use. You can of course recite parrot fashion "rewire" but it unreasonable to expect consumers to "upgrade" their wiring every time a picture guide book "requires" it. I certainly wouldnt, and I would like an answer, instead of this repetitive waffle, how is this topics wiring DANGEROUS?

    Regards, UKPN
Reply
  • Twisting words. 

     Wiring , to a previous ed, (14th) is "not necessarily unsafe" This wiring is not unsafe. 

    It is unreasonable to rewire this lighting circuit. 

    There are millions of buildings wired to previous eds, far outweighing any wired to the 18thed. more probably to the 14thed than any other. There are many with a water main/rod earth with an excellent ELI. They are safe for continued use. You can of course recite parrot fashion "rewire" but it unreasonable to expect consumers to "upgrade" their wiring every time a picture guide book "requires" it. I certainly wouldnt, and I would like an answer, instead of this repetitive waffle, how is this topics wiring DANGEROUS?

    Regards, UKPN