New EICR "unsatisfactory" - complete rewire required?!?

Former Community Member
Former Community Member
The lighting circuit has no CPC (earth), this is not uncommon in older houses. For that reason all light fittings are Class 2 i.e. plastic with no metal, and there is a clause in the tenancy agreement which forbids tampering with the light fittings (this is a house we own and rent out).


Previous EICRs did not even mention the lighting circuit because of the Class 2 fittings. I have just got a new EICR with an observation "lighting circuits have little or no earth" and classification code C1 ("Danger present, risk of injury, immediate remedial action required"). The overall assessment says "Unsatisfactory" with the comment "Needs updating to current regs". This can only be fixed by a complete rewire of the whole lighting circuit.


This is pointless, there are no earth connections in the plastic fittings.


Any thoughts? Many thanks.
Parents
  • I think there was a general consensus that the circuit should have been coded C3 (at least before the complicating factor of wooden back boxes was mentioned). The debate has been instead been around what, legally, the landlord should do once given an erroneous C1. This is not something that has an obvious answer, given that it is new untested law, and law that has been badly drafted and insists on rented dwelling being 18th Ed compliant. And that we're not lawyers.
Reply
  • I think there was a general consensus that the circuit should have been coded C3 (at least before the complicating factor of wooden back boxes was mentioned). The debate has been instead been around what, legally, the landlord should do once given an erroneous C1. This is not something that has an obvious answer, given that it is new untested law, and law that has been badly drafted and insists on rented dwelling being 18th Ed compliant. And that we're not lawyers.