New EICR "unsatisfactory" - complete rewire required?!?

Former Community Member
Former Community Member
The lighting circuit has no CPC (earth), this is not uncommon in older houses. For that reason all light fittings are Class 2 i.e. plastic with no metal, and there is a clause in the tenancy agreement which forbids tampering with the light fittings (this is a house we own and rent out).


Previous EICRs did not even mention the lighting circuit because of the Class 2 fittings. I have just got a new EICR with an observation "lighting circuits have little or no earth" and classification code C1 ("Danger present, risk of injury, immediate remedial action required"). The overall assessment says "Unsatisfactory" with the comment "Needs updating to current regs". This can only be fixed by a complete rewire of the whole lighting circuit.


This is pointless, there are no earth connections in the plastic fittings.


Any thoughts? Many thanks.
Parents
  • Alan Capon:

    You could take the view that if you have been receiving a C3 or it’s predecessor every time for 20 years, then there has been plenty of time to improve things, especially in a commercial environment, although BS7671 does not set a time limit on things.


    Or you could interpret it as a kindly slap on the wrist and see no reason to do anything.


    In this case, I feel sure that the OP has got the message. ?


Reply
  • Alan Capon:

    You could take the view that if you have been receiving a C3 or it’s predecessor every time for 20 years, then there has been plenty of time to improve things, especially in a commercial environment, although BS7671 does not set a time limit on things.


    Or you could interpret it as a kindly slap on the wrist and see no reason to do anything.


    In this case, I feel sure that the OP has got the message. ?