New EICR "unsatisfactory" - complete rewire required?!?

Former Community Member
Former Community Member
The lighting circuit has no CPC (earth), this is not uncommon in older houses. For that reason all light fittings are Class 2 i.e. plastic with no metal, and there is a clause in the tenancy agreement which forbids tampering with the light fittings (this is a house we own and rent out).


Previous EICRs did not even mention the lighting circuit because of the Class 2 fittings. I have just got a new EICR with an observation "lighting circuits have little or no earth" and classification code C1 ("Danger present, risk of injury, immediate remedial action required"). The overall assessment says "Unsatisfactory" with the comment "Needs updating to current regs". This can only be fixed by a complete rewire of the whole lighting circuit.


This is pointless, there are no earth connections in the plastic fittings.


Any thoughts? Many thanks.
Parents
  • Former Community Member
    0 Former Community Member
    UKPN:

    trusted the agent to engage this amateur.




    I've not mentioned an agent, there is no agent.

     



    UKPN:


    No, go to the council/trading standards, and ask why, after repeated requests to explain how this is a "danger to life" which requires immediate remedy, the guy wont answer. Because he cant answer, it isnt dangerous. It wasnt dangerous in 1970, the cable hasnt deteriorated, all ins fitting, RCD. nothing has changed.




    Steady on! The electrician replied, see https://communities.theiet.org/discussions/viewtopic/1037/26815#p147002 (post near bottom of p2).  While we disagree on the C1, I'm taking his advice and making improvements.


    Thanks to all for the continued posts, it is very enlightening.


Reply
  • Former Community Member
    0 Former Community Member
    UKPN:

    trusted the agent to engage this amateur.




    I've not mentioned an agent, there is no agent.

     



    UKPN:


    No, go to the council/trading standards, and ask why, after repeated requests to explain how this is a "danger to life" which requires immediate remedy, the guy wont answer. Because he cant answer, it isnt dangerous. It wasnt dangerous in 1970, the cable hasnt deteriorated, all ins fitting, RCD. nothing has changed.




    Steady on! The electrician replied, see https://communities.theiet.org/discussions/viewtopic/1037/26815#p147002 (post near bottom of p2).  While we disagree on the C1, I'm taking his advice and making improvements.


    Thanks to all for the continued posts, it is very enlightening.