New EICR "unsatisfactory" - complete rewire required?!?

Former Community Member
Former Community Member
The lighting circuit has no CPC (earth), this is not uncommon in older houses. For that reason all light fittings are Class 2 i.e. plastic with no metal, and there is a clause in the tenancy agreement which forbids tampering with the light fittings (this is a house we own and rent out).


Previous EICRs did not even mention the lighting circuit because of the Class 2 fittings. I have just got a new EICR with an observation "lighting circuits have little or no earth" and classification code C1 ("Danger present, risk of injury, immediate remedial action required"). The overall assessment says "Unsatisfactory" with the comment "Needs updating to current regs". This can only be fixed by a complete rewire of the whole lighting circuit.


This is pointless, there are no earth connections in the plastic fittings.


Any thoughts? Many thanks.
Parents
  • Chris Pearson:
    Sparkingchip:

    And surprising you can often pull cables down the wall behind the capping.


    I assume that you pull in the new cable as you take out the old - how do you join them?




    I'd cut away about half the width of each cable for 6" or so at the end of the new and old cables - place the cut edges together to and wrap tightly with insulating type (just overlapping) starting from the end that'll be drawn in last - that way you have a reasonably secure joint that's only a fraction of a mm thinker than the cables and should draw through most holes that the original cable fitted through.


      -  Andy.


Reply
  • Chris Pearson:
    Sparkingchip:

    And surprising you can often pull cables down the wall behind the capping.


    I assume that you pull in the new cable as you take out the old - how do you join them?




    I'd cut away about half the width of each cable for 6" or so at the end of the new and old cables - place the cut edges together to and wrap tightly with insulating type (just overlapping) starting from the end that'll be drawn in last - that way you have a reasonably secure joint that's only a fraction of a mm thinker than the cables and should draw through most holes that the original cable fitted through.


      -  Andy.