Two DNO 11Kv/400/230v transformers on different HV lines originally supplied two separate buildings on an industrial site. The two separate buildings are now one large steel framed one. So we have two DNO intakes and no clear demarcation within the installation. I remember reading somewhere about issues arising in such situations but cannot find the article. I am keen to establish if any issues are serious enough to seek alternatives. One of the intakes has a Biomass plant feed-in with g59 relay. Both intakes are circa 1MVA.
There are almost two different things to consider. Firstly the LV interleaving, which may make isolation in an emergency tricky, and where earth fault currents flow, if there is a fault that returns via the wrong CPC.- but that is true in any building with 2 LV supplies. (and in some cases one supply ends up having to be TT and the other TN if they are neither separated nor tightly tied together such as second supplies for certain type of fire system)
Then the HV side - are these underground lines bringing in an HV earth on the armour with them and if not how are the HV earths arranged. Presumably they are supplied by the same DNO, but are they private transformers, or if they are DNO property do they have an opinion as to how they are wired and how they should be interconnected or not . I presume they are not side by side on a common ground plane.
There are almost two different things to consider. Firstly the LV interleaving, which may make isolation in an emergency tricky, and where earth fault currents flow, if there is a fault that returns via the wrong CPC.- but that is true in any building with 2 LV supplies. (and in some cases one supply ends up having to be TT and the other TN if they are neither separated nor tightly tied together such as second supplies for certain type of fire system)
Then the HV side - are these underground lines bringing in an HV earth on the armour with them and if not how are the HV earths arranged. Presumably they are supplied by the same DNO, but are they private transformers, or if they are DNO property do they have an opinion as to how they are wired and how they should be interconnected or not . I presume they are not side by side on a common ground plane.