mapj1:
Not wishing to second guess the IDNOs, but a building with two TNC-S LV supplies is one of those things that needs to be done carefully ?
Because in effect you have two NE bonds, and two lots of bonding that put the neutral onto the structural steel, plumbing etc, when those neutrals join up round the back via a common low impedance street network ground / DNO neutral / HV ground there is potential to have a constant load dependent voltage gradient along the building. This is similar to the metal water main serving as a second PEN in a street of houses, but with less impedance to limit the current. Even though the voltages may be fractions of a volt the currents may be tens or in an unlucky case, hundreds of amps, with all the associated magnetic fields and this is 'a complication' , and is is either avoided by tying both together very solidly - easy if side by side, less so at opposite ends of a barn, or more easily using the electrode resistance in a TT system is to reduce the potential for large circulating currents.
In the end the folk who know the network details should be the DNO, but things like building change of use of a building that was separate modules into one big one, or the addition of factory piping running between previously isolated buildings can introduce problems where there originally were none.
Why is bonding them together hard if the supplies are not adjacent (but still local to the same building)? Is this not just the case of a large section bonding conductor between them, and making sure they stay bonded? Maintaining bonding throughout is already an important safety aspect, so I don't see why we should assume this would not be done.
mapj1:
Not wishing to second guess the IDNOs, but a building with two TNC-S LV supplies is one of those things that needs to be done carefully ?
Because in effect you have two NE bonds, and two lots of bonding that put the neutral onto the structural steel, plumbing etc, when those neutrals join up round the back via a common low impedance street network ground / DNO neutral / HV ground there is potential to have a constant load dependent voltage gradient along the building. This is similar to the metal water main serving as a second PEN in a street of houses, but with less impedance to limit the current. Even though the voltages may be fractions of a volt the currents may be tens or in an unlucky case, hundreds of amps, with all the associated magnetic fields and this is 'a complication' , and is is either avoided by tying both together very solidly - easy if side by side, less so at opposite ends of a barn, or more easily using the electrode resistance in a TT system is to reduce the potential for large circulating currents.
In the end the folk who know the network details should be the DNO, but things like building change of use of a building that was separate modules into one big one, or the addition of factory piping running between previously isolated buildings can introduce problems where there originally were none.
Why is bonding them together hard if the supplies are not adjacent (but still local to the same building)? Is this not just the case of a large section bonding conductor between them, and making sure they stay bonded? Maintaining bonding throughout is already an important safety aspect, so I don't see why we should assume this would not be done.