EARTHING FAULT

Can a earth fault on a lighting circuit effect another circuit , this being ring main , only two circuits in flat, After changing a light fitting i came across an earth fault on the lighting circuit , I thought i had sorted earth fault out but the other circuit in the flat started tripping , when the lighting circuit cpc is removed from earth bar , nothing trips both circuits power up. With lighting cpc in earth bar ring main trips, not on rcbos.
Parents
  • Former Community Member
    0 Former Community Member
    Well, if IR really is 200 Ohms, then the installation is leaking over 1 amp - which may well be lethal. Have you tried breaking the sections down to find out why so low (and as above a few continuity tests


    What was the lighting circuit fault - what was the repair


    Regards


    OMS
Reply
  • Former Community Member
    0 Former Community Member
    Well, if IR really is 200 Ohms, then the installation is leaking over 1 amp - which may well be lethal. Have you tried breaking the sections down to find out why so low (and as above a few continuity tests


    What was the lighting circuit fault - what was the repair


    Regards


    OMS