IDNO Loads

HI All


Just come across the attached - a snippet from an IDNO's documentation about loads for residentials.


Loads a lot lower than I am used to - what are peoples thoughts on this?


I would not be comfortable going down that low - e.g. an all electric flat with panel rads and a 3kW cylinder - don't see how you could drop down so much.


i tend to see 4.5 to 5.5 kVA for all electric flats, lowerend being for single bed units and 5.5 for two bed

34f1d679f65a545c71d7d360a23416f6-huge-image.png
Parents
  • There are many assumptions in these numbers, and most of them are to do with cost, which is being minimised. If these were modern houses the heating requirement most of the time might well be low, say 3kW, but British weather being what it is we have snow and -20C temperatures (particularly up north or Scotland) much more often than is often realised. This means the heat pump will struggle and additional heating will also be needed. Then there are the electric vehicles, which if we all have one will need a great deal of charging power unless typical usage can also be controlled (which I hope it never can be). Then there is the cooker, washing machine etc. These figures have been pared to the absolute minimum, and I assume that load shedding will become common.
Reply
  • There are many assumptions in these numbers, and most of them are to do with cost, which is being minimised. If these were modern houses the heating requirement most of the time might well be low, say 3kW, but British weather being what it is we have snow and -20C temperatures (particularly up north or Scotland) much more often than is often realised. This means the heat pump will struggle and additional heating will also be needed. Then there are the electric vehicles, which if we all have one will need a great deal of charging power unless typical usage can also be controlled (which I hope it never can be). Then there is the cooker, washing machine etc. These figures have been pared to the absolute minimum, and I assume that load shedding will become common.