HI All


Just come across the attached - a snippet from an IDNO's documentation about loads for residentials.


Loads a lot lower than I am used to - what are peoples thoughts on this?


I would not be comfortable going down that low - e.g. an all electric flat with panel rads and a 3kW cylinder - don't see how you could drop down so much.


i tend to see 4.5 to 5.5 kVA for all electric flats, lowerend being for single bed units and 5.5 for two bed

34f1d679f65a545c71d7d360a23416f6-huge-image.png
Parents
  • Hi Alan


    I am aware these figures are to do with housing blocks and estates - my question is that the figures here seem lower than what I have seen applied to such developments before.


    I normally see a block/estate estimated at 5kVA per all electric flat (for around 50 to 100 plots) to work out the supply needed. That is what is getting put on the DNO application.


    2kVA as per those figures is a fair drop from that hence the question.


    Is 5kVA per unit considered overkill for even the smaller scale housing blocks of 50 to a hundred now (noting that the figures given stated up to 750 flats for the 2kVA allowance)?








     


Reply
  • Hi Alan


    I am aware these figures are to do with housing blocks and estates - my question is that the figures here seem lower than what I have seen applied to such developments before.


    I normally see a block/estate estimated at 5kVA per all electric flat (for around 50 to 100 plots) to work out the supply needed. That is what is getting put on the DNO application.


    2kVA as per those figures is a fair drop from that hence the question.


    Is 5kVA per unit considered overkill for even the smaller scale housing blocks of 50 to a hundred now (noting that the figures given stated up to 750 flats for the 2kVA allowance)?








     