This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

IDNO Loads

HI All


Just come across the attached - a snippet from an IDNO's documentation about loads for residentials.


Loads a lot lower than I am used to - what are peoples thoughts on this?


I would not be comfortable going down that low - e.g. an all electric flat with panel rads and a 3kW cylinder - don't see how you could drop down so much.


i tend to see 4.5 to 5.5 kVA for all electric flats, lowerend being for single bed units and 5.5 for two bed

34f1d679f65a545c71d7d360a23416f6-huge-image.png
Parents
  • The figures aren’t too far away from what we use (a DNO). When replacing LV network fuses I usually find a pickup of 2KVA per property is a pretty good estimate, although the initial pickup will be a lot higher. 


    Regards,


    Alan.
Reply
  • The figures aren’t too far away from what we use (a DNO). When replacing LV network fuses I usually find a pickup of 2KVA per property is a pretty good estimate, although the initial pickup will be a lot higher. 


    Regards,


    Alan.
Children
No Data