Chris Pearson:goldenboy1818:
They have already fitted a isolator (not fused) and room in the white box is very tight nowDoesn't help!
The height of the CU isn't a hard and fast rule, but the idea is that an occupier in a wheelchair should be able to reach it.
I would be very careful on consumer unit heights
https://www.labc.co.uk/news/dont-forget-building-regulations-part-m-change
I also wouldn’t fit a switch fuse in the meter cabinet. Have you done the 1st fix? Could you possibly fit a flush consumer unit downstairs?
Chris Pearson:goldenboy1818:
They have already fitted a isolator (not fused) and room in the white box is very tight nowDoesn't help!
The height of the CU isn't a hard and fast rule, but the idea is that an occupier in a wheelchair should be able to reach it.
I would be very careful on consumer unit heights
https://www.labc.co.uk/news/dont-forget-building-regulations-part-m-change
I also wouldn’t fit a switch fuse in the meter cabinet. Have you done the 1st fix? Could you possibly fit a flush consumer unit downstairs?