goldenboy1818:
. . . The meter tails will only be about 800mm too long and not visible . . .
Which is 27% longer than the maximum length the DNO specify.
If you did the same in my employers area, you would not get either the meter or the cutout fuse until you complied. We specify 2.500m maximum length to make it clear this is a maximum value. We would also walk away if a customers switch fuse appeared in a meter box. If there really isn’t anywhere else for it, you need to get the builder to sink a second meter box next to the one provided for the DNO’s exclusive use, and put your switch fuse in there.
Regards,
Alan.
goldenboy1818:
. . . The meter tails will only be about 800mm too long and not visible . . .
Which is 27% longer than the maximum length the DNO specify.
If you did the same in my employers area, you would not get either the meter or the cutout fuse until you complied. We specify 2.500m maximum length to make it clear this is a maximum value. We would also walk away if a customers switch fuse appeared in a meter box. If there really isn’t anywhere else for it, you need to get the builder to sink a second meter box next to the one provided for the DNO’s exclusive use, and put your switch fuse in there.