This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

Which version of BS 7671 should I use?

I'm confused. Let's, for example, say I'm doing an upmarket domestic (complete with PV and EV) that's intended to be rented out and the work will be overseen by building control.


As I see it:
  • BS 7671 says I should use the latest version (subject to any transition periods when new versions are published) - so currently BS 7671:2018+A1:2020 (plus possibly a Corrigendum or so).

  • The ESQCR (as amended) demands that (because I have on-site generation operating in parallel with the mains) I comply with "British Standard Requirements" which it defines as BS 7671:2008 (17th Ed) (unamended).

  • AD P suggests that if I want a nice "deemed to comply" solution that BC will accept, I need to work to BS 7671:2008 incorporating Amendment No 1:2011.

  • As the property is going to be rented, the new "The Electrical Safety Standards in the Private Rented Sector (England) Regulations 2020" will have to be complied with, and that requires compliance with BS 7671:2018 (unamended).


So do I have to read four different versions of the Wiring Regs at once and try and come up with a design that simultaneously satisfies all four? (which I'm not sure would always be possible) and even if I did that which version should the certificate say it complies with?


  - Andy.
Parents
  • Harry Macdonald:

    Good point AJJewsbury, but can anyone think of a requirement in the current Regs that is actually prohibited in an earlier version.

    If not, then an installation to the current Regs would satisfy all of them.


    This is actually rather complicated, since the Regs are not normally legally binding. They are a standard, compliance with which is considered to be a presumption of meeting the safety requirements/duty of care. Compliance with a more up to date standard is always considered to be as safe as (or possibly safer than) compliance with the original standard and is therefore acceptable as an alternative to an earlier standard in such an instance, on the basis that standards never reduce safety when they are revised. However where the legal text specifically states a particular edition of a standard this may not be a valid assumption. It doesn't even need to be something required/prohibited but just a difference in the requirement that means an installation meets a later standard but not an earlier one.

    The safest approach is to ensure that the installation meets all editions of the standard cited, though if there are contradictions you have got your work cut out.


Reply
  • Harry Macdonald:

    Good point AJJewsbury, but can anyone think of a requirement in the current Regs that is actually prohibited in an earlier version.

    If not, then an installation to the current Regs would satisfy all of them.


    This is actually rather complicated, since the Regs are not normally legally binding. They are a standard, compliance with which is considered to be a presumption of meeting the safety requirements/duty of care. Compliance with a more up to date standard is always considered to be as safe as (or possibly safer than) compliance with the original standard and is therefore acceptable as an alternative to an earlier standard in such an instance, on the basis that standards never reduce safety when they are revised. However where the legal text specifically states a particular edition of a standard this may not be a valid assumption. It doesn't even need to be something required/prohibited but just a difference in the requirement that means an installation meets a later standard but not an earlier one.

    The safest approach is to ensure that the installation meets all editions of the standard cited, though if there are contradictions you have got your work cut out.


Children
No Data