Sparkingchip:
Just how can An AFDD like this be installed in an UK tin can consumer unit?
See four posts up the page for details. What seems rather odd is that when you look up these devices, it says nothing about the type of CU which is required. It took quite a bit of searching to find the answer.
Chris Pearson:Sparkingchip:
Just how can An AFDD like this be installed in an UK tin can consumer unit?See four posts up the page for details. What seems rather odd is that when you look up these devices, it says nothing about the type of CU which is required. It took quite a bit of searching to find the answer.
The fourteen mod consumer unit in the illustration supplies three circuits.
main switch = 2
SPD = 2
3 x AFDD = 9
1 x unusable = 1
Total = 14
The double stacked CU could supply around eleven circuits bearing in mind AFDD are not required on lighting circuits, I am not sure if you can transition from the dual pole to single pole busbar to fit one mod MCBs or RCBOs next to AFDD.
They seem to think that three AFDD would be sufficient in an installation with the majority of circuits not being protected by them.
That rules out retrofitting them as replacements in the majority of homes.
Andy B.
Sparkingchip:
A visit to the Hager German website reveals a range of screw-less Hager AFDD which clip onto a two pole busbar and have push fit cable connections on top of them.
We are do even vaguely in the same ballpark as the rest of Europe and definitely not on the same pitch playing the same game, we have been left way behind.
Andy Betteridge
And the range only goes up to 25 amps, so you can forget UK 32 amp socket ring circuits.
The double stacked CU could supply around eleven circuits bearing in mind AFDD are not required on lighting circuits. That rules out retrofitting them as replacements in the majority of homes.
AJJewsbury:
Double stacked (two row) CUs probably aren't acceptable on new builds either if you need to meet AD-M's requirements of the toggles being within a 100m band between 1350mm and 1450mm above floor level - if one row is within that range the other one isn't likely to be...
It isn't a requirement in an ordinary visitable dwelling; it is merely a recommendation in the Approved Document.
Chris Pearson:AJJewsbury:
Double stacked (two row) CUs probably aren't acceptable on new builds either if you need to meet AD-M's requirements of the toggles being within a 100m band between 1350mm and 1450mm above floor level - if one row is within that range the other one isn't likely to be...It isn't a requirement in an ordinary visitable dwelling; it is merely a recommendation in the Approved Document.
As I understand it there is a requirement for accessibility - and AD-M gives examples that satisfy the requirement - while we are of course free to meet the requirements in other ways if we choose, how could we hope to demonstrate compliance if we put things outside of that range? How could we make something that was outside of that range just as accessible?
- Andy.