Mikey70:
Thanks for the responses. Graham, yes it is via an DNO supply, although it is buried supply cables with a TX on a pole located adjacent the Switch Room.
If with this type of PNB supply PME conditions apply then yes TT connection using a time delay RCD (instead of the MCB), earth rod at the container, RCBO's to the outgoing circuits.
If not PME then would the original proposal be meet the guidance ie PNB supply via private TX ?
Thanks.
If the supply is an installation with a couple of sources such as a generator and privately-operated transformer, where the N-E bond is made at the switchboard (instead of separately at the generator and transformer) to prevent circulating currents, then that is technically PNB, but:
(a) PME conditions do not apply; and
(b) You can generally consider the installation downstream of the main switchboard as TN-S.
Mikey70:
Thanks for the responses. Graham, yes it is via an DNO supply, although it is buried supply cables with a TX on a pole located adjacent the Switch Room.
If with this type of PNB supply PME conditions apply then yes TT connection using a time delay RCD (instead of the MCB), earth rod at the container, RCBO's to the outgoing circuits.
If not PME then would the original proposal be meet the guidance ie PNB supply via private TX ?
Thanks.
If the supply is an installation with a couple of sources such as a generator and privately-operated transformer, where the N-E bond is made at the switchboard (instead of separately at the generator and transformer) to prevent circulating currents, then that is technically PNB, but:
(a) PME conditions do not apply; and
(b) You can generally consider the installation downstream of the main switchboard as TN-S.