AJJewsbury:
PME would still be a point to consider though. As Graham suggested, PNB isn't usually really TN-C-S (but can be in some rare circumstances - e,g. where the Tx serves more than one customer) and by definition isn't PME (as there's no requirement for multiple earthing),
Hi Andy,
If it's a DNO-provided PNB, then usually PME conditions apply (see G12/4), especially where the N-E bond is made at the service head. In rare cases, where the N-E bond is made in one place only for all customers, the DNO may declare TN-S (usually older supplies).
AJJewsbury:
PME would still be a point to consider though. As Graham suggested, PNB isn't usually really TN-C-S (but can be in some rare circumstances - e,g. where the Tx serves more than one customer) and by definition isn't PME (as there's no requirement for multiple earthing),
Hi Andy,
If it's a DNO-provided PNB, then usually PME conditions apply (see G12/4), especially where the N-E bond is made at the service head. In rare cases, where the N-E bond is made in one place only for all customers, the DNO may declare TN-S (usually older supplies).