AJJewsbury:
Will the container really be a 'mobile or transportable unit' as far as the wiring is concerned? E.g. is it likely to be moved elsewhere and just hooked up to another supply?
717.1 (ii) - but I agree if it's not readily "transportable" then perhaps 717 doesn't apply - but it's still a metal-frame structure, and as the forum user known as UKPN has quite rightly stated in another thread along these lines recently, in some cases where PME conditions apply, particularly rural, it may well be best to follow the same rules as Section 717 in any case.
AJJewsbury:
Will the container really be a 'mobile or transportable unit' as far as the wiring is concerned? E.g. is it likely to be moved elsewhere and just hooked up to another supply?
717.1 (ii) - but I agree if it's not readily "transportable" then perhaps 717 doesn't apply - but it's still a metal-frame structure, and as the forum user known as UKPN has quite rightly stated in another thread along these lines recently, in some cases where PME conditions apply, particularly rural, it may well be best to follow the same rules as Section 717 in any case.