This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

EICR code for a “Shall”.

Given that a Wiring Regulation containing the word “Shall” is not optional, but a definite requirement, can an existing installation that does not comply be coded 3-Improvement recommended rather than code 2-Potentially dangerous - urgent remedial action required?


Andy B.
Parents
  • I'll use an example of 514.4.4, which is a "shall" requirement - 'Other conductors shall be identified by colour in accordance with Table 51.'


    So, I have an installation in which the blue switched lines (switch returns) on a lighting circuit have not been overmarked brown.


    Are you proposing C2 for that?
Reply
  • I'll use an example of 514.4.4, which is a "shall" requirement - 'Other conductors shall be identified by colour in accordance with Table 51.'


    So, I have an installation in which the blue switched lines (switch returns) on a lighting circuit have not been overmarked brown.


    Are you proposing C2 for that?
Children
No Data