EICR code for a “Shall”.

Given that a Wiring Regulation containing the word “Shall” is not optional, but a definite requirement, can an existing installation that does not comply be coded 3-Improvement recommended rather than code 2-Potentially dangerous - urgent remedial action required?


Andy B.
Parents
  • Graham's example is along the lines of what I would have chosen. Non compliance is not necessarily immediately dangerous. To give a slightly different example, if one neglects to affix a warning notice i.a.w. 514.14.1, how does that present any form of immediate danger?
Reply
  • Graham's example is along the lines of what I would have chosen. Non compliance is not necessarily immediately dangerous. To give a slightly different example, if one neglects to affix a warning notice i.a.w. 514.14.1, how does that present any form of immediate danger?