Given that a Wiring Regulation containing the word “Shall” is not optional, but a definite requirement, can an existing installation that does not comply be coded 3-Improvement recommended rather than code 2-Potentially dangerous - urgent remedial action required?


Andy B.
Parents
  • Agreed Simon Barker, but we are discussing the application of that in terms of the "coding" in BS 7671.


    This appears ONLY in Appendix 6 - which is "Informative" - i.e. "guidance", and definitely not "shall" ... which adds another level of complexity to the whole issue.
Reply
  • Agreed Simon Barker, but we are discussing the application of that in terms of the "coding" in BS 7671.


    This appears ONLY in Appendix 6 - which is "Informative" - i.e. "guidance", and definitely not "shall" ... which adds another level of complexity to the whole issue.