Additional socket, domestic

Having been asked to fit a new weatherproof external socket to a domestic property, it's not feasible to fit the easy way, back-to-back, but perfectly possible and, I would expect, acceptable to fit it at the end of a 2m horizontal length of PVC conduit.  HOWEVER, the client would also like a new internal socket back-to-back from this position.  Is it considered acceptable to extend the ring circuit through the conduit to this new location - OK, I'd upgrade to galv steel - whilst keeping the external socket as a fused spur?  Location is adjacent to the path from gate to front door.  All other requirements (RCD etc) are satisactory.
Parents
  • 3. Only one single or one double socket is permitted on a spur.

    On an unfused spur that is - you are permitted more sockets on a fused spur, although you should ensure that the total loading would be unlikely to exceed 13A nominal.


       - Andy.
Reply
  • 3. Only one single or one double socket is permitted on a spur.

    On an unfused spur that is - you are permitted more sockets on a fused spur, although you should ensure that the total loading would be unlikely to exceed 13A nominal.


       - Andy.