Additional socket, domestic

Having been asked to fit a new weatherproof external socket to a domestic property, it's not feasible to fit the easy way, back-to-back, but perfectly possible and, I would expect, acceptable to fit it at the end of a 2m horizontal length of PVC conduit.  HOWEVER, the client would also like a new internal socket back-to-back from this position.  Is it considered acceptable to extend the ring circuit through the conduit to this new location - OK, I'd upgrade to galv steel - whilst keeping the external socket as a fused spur?  Location is adjacent to the path from gate to front door.  All other requirements (RCD etc) are satisactory.
Parents
  • was really whether part of an 'indoors' circuit i.e. the cables of the ring extended to serve a new internal socket, could be run 'outdoors' in conduit on the face of the external wall

    Basically the regs don't offer any opinion - there's generally no difference in requirements for wiring run indoors or outdoors (just the same general requirement that it be suitable for its environment).


     
    David's comment about fault conditions relates, I presume, to possible loss of neutral on TN-C-S

    Broken PENs is certainly one (even the main) concern, but there are also risks from other faults - e.g. normal L-PE faults that can take up to 5s to clear - or even longer if they occur on the DNO side.

    I have slightly lower confidence in the ability of PVC conduit and saddles/clips to withstand probable impacts from users of the path.

    There are several gauges of PVC conduit - heavy gauge is more expensive and less readily available but is a fair bit more robust than the light guage you usually find in most DIY sheds and the like.


    Alternatively you could put sheathed cables in unearthed steel conduit - a common approach on the continent - and not against the regs if done properly ... although likely to raise an eyebrow (or even a howl or two) from traditional UK types.


      - Andy.
Reply
  • was really whether part of an 'indoors' circuit i.e. the cables of the ring extended to serve a new internal socket, could be run 'outdoors' in conduit on the face of the external wall

    Basically the regs don't offer any opinion - there's generally no difference in requirements for wiring run indoors or outdoors (just the same general requirement that it be suitable for its environment).


     
    David's comment about fault conditions relates, I presume, to possible loss of neutral on TN-C-S

    Broken PENs is certainly one (even the main) concern, but there are also risks from other faults - e.g. normal L-PE faults that can take up to 5s to clear - or even longer if they occur on the DNO side.

    I have slightly lower confidence in the ability of PVC conduit and saddles/clips to withstand probable impacts from users of the path.

    There are several gauges of PVC conduit - heavy gauge is more expensive and less readily available but is a fair bit more robust than the light guage you usually find in most DIY sheds and the like.


    Alternatively you could put sheathed cables in unearthed steel conduit - a common approach on the continent - and not against the regs if done properly ... although likely to raise an eyebrow (or even a howl or two) from traditional UK types.


      - Andy.