Kelly Marie:
I've been reading about the fact that a bit of DC on the mains can cause toroidal transformers to hum more than normal. So I decided to try to measure it I've got no toroidal transformers I'm just interested to try to measure it. Any how I ran a 150 watt bulb via a half way rectifier and got around 480 millivolts DC from neutral to earth and around 10 millivolts live to earth and live to neutral I then reversed the diode but still the voltage was only from neutral to earth why would this be? Incidentally with the diode the other way round the earth was 480 millivolts POSITIVE to neutral. The way I measured it was with my best quality meter ( the true RMS 6000 count one) switched to DC Volts range. My other meters couldn't make sense of anything when connected to the test terminals on DC range with AC mains present. Why could I only measure the offset on the neutral side? Surely it shoul be present on both sides.
The answer is, most likely, the resistance of the Neutral between the "point of common coupling" between N and PE.
... and that is the reason that Neutral is a Live conductor!
To explain further, a half-wave rectified DC signal as both AC and DC components. The AC components "cancel" in your multimeter, so you are left with the DC component. Other meter types will react differently depending on how they "average" the voltage ... that is the only difference between a "true rms" and "normal" multimeter, the way they "average" the voltage (or current, or power).
Kelly Marie:
I've been reading about the fact that a bit of DC on the mains can cause toroidal transformers to hum more than normal. So I decided to try to measure it I've got no toroidal transformers I'm just interested to try to measure it. Any how I ran a 150 watt bulb via a half way rectifier and got around 480 millivolts DC from neutral to earth and around 10 millivolts live to earth and live to neutral I then reversed the diode but still the voltage was only from neutral to earth why would this be? Incidentally with the diode the other way round the earth was 480 millivolts POSITIVE to neutral. The way I measured it was with my best quality meter ( the true RMS 6000 count one) switched to DC Volts range. My other meters couldn't make sense of anything when connected to the test terminals on DC range with AC mains present. Why could I only measure the offset on the neutral side? Surely it shoul be present on both sides.
The answer is, most likely, the resistance of the Neutral between the "point of common coupling" between N and PE.
... and that is the reason that Neutral is a Live conductor!
To explain further, a half-wave rectified DC signal as both AC and DC components. The AC components "cancel" in your multimeter, so you are left with the DC component. Other meter types will react differently depending on how they "average" the voltage ... that is the only difference between a "true rms" and "normal" multimeter, the way they "average" the voltage (or current, or power).