Landlord electrical safety certificate

Hi all, my father in law has a rental property that was completely rewired and with new split load CU five years ago. The installation is now due an inspection. Will the fact that the CU is plastic constitute a "fail"?

Parents
  • Former Community Member
    0 Former Community Member
    Extract from the above topic:

     
    OlympusMons

    Forum topic level 1Forum replies level 4Social sharer level 0

    118 Posts

    Well if you are confused Andy, what chance do the rest of us have?


    Heres my take on it;

    115.1 (2018) says "For installations over which a licensing or other authority exercises a statutory control, the requirements of that authority shall be ascertained and complied with in the design and execution of the installation"

    The 2020 rented regs confer statutory duties on local housing authorities to enforce the regulations, they therefore have statutory control. And these reference BS7671:2018 unammended.

    BS7671:2008 also has 115.1 with exactly the same wording. So all roads lead to BS7671:2018 unammended. Simples


    Regards


    BOD
Reply
  • Former Community Member
    0 Former Community Member
    Extract from the above topic:

     
    OlympusMons

    Forum topic level 1Forum replies level 4Social sharer level 0

    118 Posts

    Well if you are confused Andy, what chance do the rest of us have?


    Heres my take on it;

    115.1 (2018) says "For installations over which a licensing or other authority exercises a statutory control, the requirements of that authority shall be ascertained and complied with in the design and execution of the installation"

    The 2020 rented regs confer statutory duties on local housing authorities to enforce the regulations, they therefore have statutory control. And these reference BS7671:2018 unammended.

    BS7671:2008 also has 115.1 with exactly the same wording. So all roads lead to BS7671:2018 unammended. Simples


    Regards


    BOD