Hi all, my father in law has a rental property that was completely rewired and with new split load CU five years ago. The installation is now due an inspection. Will the fact that the CU is plastic constitute a "fail"?

  • davezawadi (David Stone):

    Alcomax

    The only way to give an EICR to a landlord, where it is necessary to be completely compliant with BS7671, is to have no limitations. If you say "I didn't inspect x, y or z because..., the installation may not be compliant, and therefore not meet the law as described. If I say "I did not check this circuit, or I couldn't inspect under the floor although I knew there was a junction box or....." you see it just goes on. Limitations should be few and simple with good reasons. I have seen EICRs where basically nothing useful was inspected or tested because of a string of reasons, even including "I could not inspect the CU because the cupboard was full of junk". So a quick visual of what could be seen and a satisfactory installation. Is that the standard which you think should be met, because if so I know a couple of dodgy landlords who would find you jolly useful!


    What company you frequent is your own business.

    "The only way to give an EICR to a landlord, where it is necessary to be completely compliant with BS7671, is to have no limitations. "


    The above is nonsensical. The nearest scenario could possibly be a Regularisation for BC purposes, even then there would be agreed limitations.


    I suggest you have a read of Guidance Note 3.


    To be clear, "where it is necessary to be completely compliant with BS7671" is for new works and additions. Read into the new law what you will, but it is written in usual legal jargon expressly  to allow for the application of reasonableness.


    The gist is that the Inspector has to know what they are doing and be able to back it up. Anyone doing remedial's afterwards has to do this Installation work fully compliant with BS7671, so an electrical installation certificate and/or minor works certificate for these works.


    There seems to be a determination to sow seeds of doubts in the minds of electricians conducting EICR for rental. Would this be due to their being vested interests in making money out of  this fey "confusion"?


  • Alcomax:



    There seems to be a determination to sow seeds of doubts in the minds of electricians conducting EICR for rental. Would this be due to their being vested interests in making money out of  this fey "confusion"?



    I have no issues about folk making money out of these new regulations and it would be nice if the inspection activity was as fastidious as some have studied the law associated with them. I try to stay well clear of the domestic sector but I have to dip the toe in on occasions. Last week I did a two up two down terrace house on my own. I charged £160 plus vat. I can tell you that although I took my time and was very measured, I certainly wouldnt have wanted to be going to another one on that day. The landlord moaned a bit because another lad had quoted £120 plus vat but he wasnt available for several weeks. People might be making a few quid but if they are doing it right at those prices, they deserve it!


  • Lyle, I did not have electricians in mind! Just those in splendid isolation and pass judgement remotely. The market level for rental was set long ago and I do not expect it to change much for electricians.


    Perhaps, like yourself, I was priced out of the domestic rental arena years ago, about 2005/6. However, this new law seems to be big news as I have been inundated with requests from landlords the last few weeks. It usually goes along the lines of  "how much?" , then varying levels of abuse and some fumbled attempt at pulling my heart strings with "but I am a businessman/woman striving to make a living and how am I able to do that and help all those poor tenants if I have to pay more than a hundred quid?"



    Out of interest I pitched a couple of one bed flats at £160 each to see how the rough end has developed since I left it in 2006 . Wow....part P has a lot to answer for. These had been let for 15 years. Regularly "tested" as per landlord parlance and the most dangerous dwellings I have ever Inspected.
  • What limitations do you think are reasonable Alcomax? I see non-compliance as an issue everywhere, because there is scope enough if the installation is sound in BS7671. Some examples would be useful from you, to discuss.


    My first problem would be with the inspector if he (she) does not have a level 3 qualification in inspection for EICRs, ie 2391 or 2395 themselves (NO QS here), and considerable verifiable experience working with an experienced inspector. This puts 90% of inspections off the chart to start with. You can see that the price is the only criterion that interests the landlord from Lyle, and anyone can easily do virtually nothing for 50 quid and fill something into the form. I consider that this really does matter to get this right from the start.
  • davezawadi (David Stone):

    Alcomax

    The only way to give an EICR to a landlord, where it is necessary to be completely compliant with BS7671, is to have no limitations. If you say "I didn't inspect x, y or z because..., the installation may not be compliant, and therefore not meet the law as described. If I say "I did not check this circuit, or I couldn't inspect under the floor although I knew there was a junction box or....." you see it just goes on. Limitations should be few and simple with good reasons. I have seen EICRs where basically nothing useful was inspected or tested because of a string of reasons, even including "I could not inspect the CU because the cupboard was full of junk". So a quick visual of what could be seen and a satisfactory installation. Is that the standard which you think should be met, because if so I know a couple of dodgy landlords who would find you jolly useful!


    But provided that the landlord is clutching a report that shows no defects, then nobody has any way to tell that the installation is non-compliant.  If you only have to find a blind electrician every five years, you could go for decades without anybody being any the wiser.  The report just has to look plausible enough to get it past the council.


    What it needs is a limitation that's an encoded way to say "I wasn't actually asked to look at the installation; the landlord described it to me over the phone, and it sounds compliant".


  • I have carried out 5 EICRs in the last month for PRS .


    All 5 failed or should that be "Unsatisfactory "?


    One clocked up a C1 for a missing cover from a bathroom pull switch with conductor strands sticking out of the terminals that could be touched with a raised arm. Before someone asks I made it safe at the time of inspection.


    Same premises had an operational limitation, "No inspection or testing inside the consumer unit due to the presence of asbestos". A warning label was applied to the CU indicating the presence of asbestos.


    One premises was rewired 5 years ago to a high standard but clocked up a C2 as one of the MK RCDs failed to trip on the instrument tests or the test button. A C3 for a plastic consumer unit installed before January 2016. I don't care where the CU is in the premises it is a non-compliance so. I record it. I am risk averse so why would I not record it? If I don't and something happens the client I am in no doubt would say ," If you had informed me I would have had it replaced". A blatant lie but a good basis for a claim against me. If I report it and something happens they could be up to their eyes in SH 1T for ignoring my recommendation and a basis for an insurance company to refuse a claim. 


    Another flat had a limitation for no access to the supply fuse as it was locked in a cupboard and none of my FP keys fitted.
  • Tu quoque David,


    The best I can suggest to you is to ask your dodgy landlord mates to get their Installation works done to standard in the first instance, then there would not be the need for all this faffing about with consultants wanting to regularise everything after the event with an EICR. That is not what an EICR is for and the new rental law is not saying regularise with an EICR.


    For someone who claims to have taught 2391, I am alarmed that you have to ask about limitations to inspections. It seems you want a one size fits all of "no limitations".

    If I have sight of a Report with no limitations, the first thing I suspect is a drive by or a blue peter style "satisfactory report", usually with every inspection box ticked and every box in the schedules with some random number in it. So David, if you are convinced that rental EICR should be conducted erroneously as initial verification, please keep it to yourself as it is not helpful.


    A nice simple answer to " what limitations are reasonable?"


    The ones that you agreed with the client in advance in writing.


  • Can the client therefore stipulate any limitation they want?


    For example: do not inspect construction material of the consumer unit.
  • geoffsd:

    Can the client therefore stipulate any limitation they want?


    For example: do not inspect construction material of the consumer unit.


    ?    Cheeky.


    I think it best that the inspector sets those!


    They can stipulate their requirements , you stipulate yours. If its something unreasonable as above, then you would be a fool to accept the contract. As this is clearly then a "dodgy landlord", then play them at there own  game, having taken payment in advance, you say the construction of the unit is fundamental in deciding the outcome and so attribute FI [ futher investigation] to the temporarily "invisible" consumer unit.


  • I did an inspection and test today for a landlords safety inspection.


    Square D Qwikline II consumer unit installed around 2004 with a steel back box and face plate, but  a plastic visor over the devices. Nearly, but not quite.


    Andy B.