SPD on TT system

6bf4417090a42c9e22fd39bd0931f8e7-huge-502858c5-e119-40f1-9c4d-cdc78b4069c4.jpg

This is on a TT system. Just wondering what the essential difference is between a TN and TT connection and the consequences if it is incorrect.
Parents
  • Only true to say that N and E are at the same voltage if you are close to the point of junction, and exactly what close means depends on the pulse duration, and to a lesser extent what else is connected to earth but not to the neutral that will increase the capacitance to terra firma. But if you are more than perhaps 6 feet away the they can be 1000+ volts apart for a few microseconds during a kA surge.


    But in the TT suppression there is a spark gap or at least a gas discharge device in the earth path, as semiconductors may fail short, but not fire the ADS properly In a TN system the semiconductors can go to ground and fuses will handle it.
Reply
  • Only true to say that N and E are at the same voltage if you are close to the point of junction, and exactly what close means depends on the pulse duration, and to a lesser extent what else is connected to earth but not to the neutral that will increase the capacitance to terra firma. But if you are more than perhaps 6 feet away the they can be 1000+ volts apart for a few microseconds during a kA surge.


    But in the TT suppression there is a spark gap or at least a gas discharge device in the earth path, as semiconductors may fail short, but not fire the ADS properly In a TN system the semiconductors can go to ground and fuses will handle it.