The blue blank plate “pops off” and there is a switch mechanism in the neutral side.
Considering the distribution cable goes up four storeys from the cellar then to the other end of the building, a run of about 80 metres, and I was swapping out the main switch in the consumer unit for a 30 mA RCD to avoid a C2 and C3’s on the report, being able to lock it off easily would be an major advantage.
My plan when I got there was to take a fuse out and put it in my pocket, but there wasn’t one to take out.
The blue blank plate “pops off” and there is a switch mechanism in the neutral side.
Considering the distribution cable goes up four storeys from the cellar then to the other end of the building, a run of about 80 metres, and I was swapping out the main switch in the consumer unit for a 30 mA RCD to avoid a C2 and C3’s on the report, being able to lock it off easily would be an major advantage.