Large rural home, family members getting shocks from water pipes when water was running. Owner got a severe shock from the outside tap. Their contractor did some investigation and ruled out a fault in the installation. As the system was TNCS it then looked like a classic case of DNO lost neutral so contractor called them in. Investigation revealed a fault in a nearby farm which was on the same single-phase transformer but was TT. They duly cut off the the offending circuit which they established was supplying the barn. They removed a 45A fuse from the distribution circuit and stuck warning tape over the fuse carrier but left the fuse. Problem solved. I was called in by the home owner when the shocks returned. Unfortunately it was late yesterday afternoon and I didn’t relish the prospect. I stuck a bit of reinforcing bar in the garden and measured 187v between that and the outside tap which was connected to a copper supply pipe. I went to the farm and the old farmer kindly gave me access. He had replaced the fuse that the DNO removed as he needed light to feed his animals but forgot to remove it again. Anyway, his own contractor had apparently dismissed the DNO diagnosis. I pulled the fuse and found that the fault voltage at the house disappeared. Further investigation revealed an almost dead short between phase and earth on a circuit in the barn. The RCD had failed. Given that it was a TT system the fault current was insufficient to blow the 45A fuse. The fault voltage in the house, I speculate, was the manifestation of the voltage drop across the DNO earth electrode. 

The situation does reflect an issue in TTing installations on a TNCS system.
Parents
  • Harry Macdonald:

    I would have thought that the farmer might receive quite an interesting electricity bill if he had anything approaching 45A continuously going from Live to Earth.


    Harry don’t forget, this is a TT installation. I measured Ra with a loop tester at 80ohms. That would have included Re but not any parallel contribution due to the metal stanchions of the old barn. The combined resistance was 26 ohms. As AJ indicated, the combined consumer resistance will have been lower than Re to see that sort of voltage division; 187v across Re and circa 230-187 across the consumer connection to earth. There appeared to be about 1ohm in the fault but all in all a little over 8A of fault current. 

    To be honest, I am sorry that I didn’t spend more time on it as it was a very interesting situation. I am almost tempted to return and re-impose the fault, if nothing else to get a photo of the MFT displaying 187v with one probe on the water tap and the other on the re-bar in the flower bed! Might even have stuck a lamp on for effect! 


Reply
  • Harry Macdonald:

    I would have thought that the farmer might receive quite an interesting electricity bill if he had anything approaching 45A continuously going from Live to Earth.


    Harry don’t forget, this is a TT installation. I measured Ra with a loop tester at 80ohms. That would have included Re but not any parallel contribution due to the metal stanchions of the old barn. The combined resistance was 26 ohms. As AJ indicated, the combined consumer resistance will have been lower than Re to see that sort of voltage division; 187v across Re and circa 230-187 across the consumer connection to earth. There appeared to be about 1ohm in the fault but all in all a little over 8A of fault current. 

    To be honest, I am sorry that I didn’t spend more time on it as it was a very interesting situation. I am almost tempted to return and re-impose the fault, if nothing else to get a photo of the MFT displaying 187v with one probe on the water tap and the other on the re-bar in the flower bed! Might even have stuck a lamp on for effect! 