RCD failure causes shock in neighbours house

Large rural home, family members getting shocks from water pipes when water was running. Owner got a severe shock from the outside tap. Their contractor did some investigation and ruled out a fault in the installation. As the system was TNCS it then looked like a classic case of DNO lost neutral so contractor called them in. Investigation revealed a fault in a nearby farm which was on the same single-phase transformer but was TT. They duly cut off the the offending circuit which they established was supplying the barn. They removed a 45A fuse from the distribution circuit and stuck warning tape over the fuse carrier but left the fuse. Problem solved. I was called in by the home owner when the shocks returned. Unfortunately it was late yesterday afternoon and I didn’t relish the prospect. I stuck a bit of reinforcing bar in the garden and measured 187v between that and the outside tap which was connected to a copper supply pipe. I went to the farm and the old farmer kindly gave me access. He had replaced the fuse that the DNO removed as he needed light to feed his animals but forgot to remove it again. Anyway, his own contractor had apparently dismissed the DNO diagnosis. I pulled the fuse and found that the fault voltage at the house disappeared. Further investigation revealed an almost dead short between phase and earth on a circuit in the barn. The RCD had failed. Given that it was a TT system the fault current was insufficient to blow the 45A fuse. The fault voltage in the house, I speculate, was the manifestation of the voltage drop across the DNO earth electrode. 

The situation does reflect an issue in TTing installations on a TNCS system.
Parents
  • presumably this is a case where the TT earth is a better connection to terra-firma than the one the DNO have for the TNC-S part of the network.

    For example if the DNO had the maximum permitted 20 ohms between their NE  star point and terra-firma proper then the  effective electrode resistance to earth to which the farm has faulted is significantly lower resistance, about 7 ohms,  so that the NE 240V is split such that 187 of the volts are dropped on the TNCS DNO electrodes, and the other 53V across the TT electrode.


    This is not a fault mechanism that is unique to TT or TNC-s systems - any system with a very low impedance fault from a live wire to true earth, such as steel piles or buried private pipelines can pull the whole mains off-balance. The problem is more likely to be serious with a rural installation with lower power pole pig transformers supplying a small number of subscribers per transformer, as the DNO side earthing is likely to be less extensive.

    There is an assumption in a most textbooks and regulations that the supply side is pretty much the most solidly earthed thing around - it is not always true, and especially a problem for temporary supplies from gensets and similar.


Reply
  • presumably this is a case where the TT earth is a better connection to terra-firma than the one the DNO have for the TNC-S part of the network.

    For example if the DNO had the maximum permitted 20 ohms between their NE  star point and terra-firma proper then the  effective electrode resistance to earth to which the farm has faulted is significantly lower resistance, about 7 ohms,  so that the NE 240V is split such that 187 of the volts are dropped on the TNCS DNO electrodes, and the other 53V across the TT electrode.


    This is not a fault mechanism that is unique to TT or TNC-s systems - any system with a very low impedance fault from a live wire to true earth, such as steel piles or buried private pipelines can pull the whole mains off-balance. The problem is more likely to be serious with a rural installation with lower power pole pig transformers supplying a small number of subscribers per transformer, as the DNO side earthing is likely to be less extensive.

    There is an assumption in a most textbooks and regulations that the supply side is pretty much the most solidly earthed thing around - it is not always true, and especially a problem for temporary supplies from gensets and similar.