RCD failure causes shock in neighbours house

Large rural home, family members getting shocks from water pipes when water was running. Owner got a severe shock from the outside tap. Their contractor did some investigation and ruled out a fault in the installation. As the system was TNCS it then looked like a classic case of DNO lost neutral so contractor called them in. Investigation revealed a fault in a nearby farm which was on the same single-phase transformer but was TT. They duly cut off the the offending circuit which they established was supplying the barn. They removed a 45A fuse from the distribution circuit and stuck warning tape over the fuse carrier but left the fuse. Problem solved. I was called in by the home owner when the shocks returned. Unfortunately it was late yesterday afternoon and I didn’t relish the prospect. I stuck a bit of reinforcing bar in the garden and measured 187v between that and the outside tap which was connected to a copper supply pipe. I went to the farm and the old farmer kindly gave me access. He had replaced the fuse that the DNO removed as he needed light to feed his animals but forgot to remove it again. Anyway, his own contractor had apparently dismissed the DNO diagnosis. I pulled the fuse and found that the fault voltage at the house disappeared. Further investigation revealed an almost dead short between phase and earth on a circuit in the barn. The RCD had failed. Given that it was a TT system the fault current was insufficient to blow the 45A fuse. The fault voltage in the house, I speculate, was the manifestation of the voltage drop across the DNO earth electrode. 

The situation does reflect an issue in TTing installations on a TNCS system.
Parents
  • Lyle


    You say the house supply was TN-C-S? You say it was a copper water pipe connected to the incoming metal water supply pipe? Was the supply pipe bonded to the incoming supply neutral?


    I can see the line to earth fault on a TT system without a functional RCD not operating the 45A fuse. I am thinking that the ground is sitting at around 0V and the outside tap is at 187V with respect to the general mass of earth as I cannot see the line to earth fault lifting the voltage of the general mass of earth to 187V some distance away from the site of the fault. 


    If the copper water pipe in the house is bonded it is directly connected to the transformer neutral so how can it sit at 187V to Earth?


    If the water pipe is not bonded and/or the transformer earth is disconnected then that is a different story.
Reply
  • Lyle


    You say the house supply was TN-C-S? You say it was a copper water pipe connected to the incoming metal water supply pipe? Was the supply pipe bonded to the incoming supply neutral?


    I can see the line to earth fault on a TT system without a functional RCD not operating the 45A fuse. I am thinking that the ground is sitting at around 0V and the outside tap is at 187V with respect to the general mass of earth as I cannot see the line to earth fault lifting the voltage of the general mass of earth to 187V some distance away from the site of the fault. 


    If the copper water pipe in the house is bonded it is directly connected to the transformer neutral so how can it sit at 187V to Earth?


    If the water pipe is not bonded and/or the transformer earth is disconnected then that is a different story.