The IET is carrying out some important updates between 17-30 April and all of our websites will be view only. For more information, read this Announcement
Chris Pearson:
My point was that it may not be PME at all. Where are those multiple electrodes and what are they achieving?
If you look at the ESQCR regulations, there only needs to be two earths to make a PME supply - one at the substation end, located at or before the connection to the first service connection, and at the far end of the PME distribution main, at or after the final service connection.
Regards,
Alan.
Chris Pearson:
My point was that it may not be PME at all. Where are those multiple electrodes and what are they achieving?
If you look at the ESQCR regulations, there only needs to be two earths to make a PME supply - one at the substation end, located at or before the connection to the first service connection, and at the far end of the PME distribution main, at or after the final service connection.
Regards,
Alan.
We're making some changes behind the scenes to deliver a better experience for our members and customers. Posting and interactions are paused. Thank you for your patience and see you soon!
For more information, please read this announcement