RCD failure causes shock in neighbours house

Large rural home, family members getting shocks from water pipes when water was running. Owner got a severe shock from the outside tap. Their contractor did some investigation and ruled out a fault in the installation. As the system was TNCS it then looked like a classic case of DNO lost neutral so contractor called them in. Investigation revealed a fault in a nearby farm which was on the same single-phase transformer but was TT. They duly cut off the the offending circuit which they established was supplying the barn. They removed a 45A fuse from the distribution circuit and stuck warning tape over the fuse carrier but left the fuse. Problem solved. I was called in by the home owner when the shocks returned. Unfortunately it was late yesterday afternoon and I didn’t relish the prospect. I stuck a bit of reinforcing bar in the garden and measured 187v between that and the outside tap which was connected to a copper supply pipe. I went to the farm and the old farmer kindly gave me access. He had replaced the fuse that the DNO removed as he needed light to feed his animals but forgot to remove it again. Anyway, his own contractor had apparently dismissed the DNO diagnosis. I pulled the fuse and found that the fault voltage at the house disappeared. Further investigation revealed an almost dead short between phase and earth on a circuit in the barn. The RCD had failed. Given that it was a TT system the fault current was insufficient to blow the 45A fuse. The fault voltage in the house, I speculate, was the manifestation of the voltage drop across the DNO earth electrode. 

The situation does reflect an issue in TTing installations on a TNCS system.
Parents
  • So (I think).

    If we have L that can be any voltage (including zero) above or below true earth and

    If we have N that can be any voltage (including zero) above or below true earth and

    we take our earth as local ground reference then an RCD might save us from Live potentials to local ground giving enough current to flow to trip it in the required time.

    If we take our earth as from something other than local ground then we might not have that
Reply
  • So (I think).

    If we have L that can be any voltage (including zero) above or below true earth and

    If we have N that can be any voltage (including zero) above or below true earth and

    we take our earth as local ground reference then an RCD might save us from Live potentials to local ground giving enough current to flow to trip it in the required time.

    If we take our earth as from something other than local ground then we might not have that