Hi all,
In terms of calculating the overall maximum demand on the whole installation i use w/m2 figures, however i do not feel comfortable doing this for individual submains. Currently my methodology usually follows looking at the connected load and applied a diversity of say 0.7 to get a circuit breaker size and thereafter put the design current to 90% of the breaker. Ie 80A breaker, design current of 72 Amps, i have done this to allow spare volt drop for any future loads on the installation, however i am not sure this is the best way to tackle building the Amtech model as it seems very wasteful.
Ive seen various posts about using w/m2 for submains, but is this figure only for use throughout a full building. Ie looking at BSRIA rules of thumb, gives 160 w/m2 for a shop. If i applied this figure for a 50m2 commercial unit within a building, this would only require a submain design current of 11.5A TP&N, which seems very small to me.
How are other designers tackling this?