Fixed diesel generator earthing

Hi folks, i'm after your knowledge again!


I have a 184KW diesel generator which is to supply a test bay for testing machines to big for the building supply.  The generated supply will not be used/connected to the building supply.

Would the earthing arrangements be as TT with a rod at the generator connected to the neutral/star connection?


Thanks in advance ?
Parents
  • It would usually have it's own rod connected to the star point & PE to the building - making it TN-S.

       - Andy.
Reply
  • It would usually have it's own rod connected to the star point & PE to the building - making it TN-S.

       - Andy.