Hi folks, i'm after your knowledge again!


I have a 184KW diesel generator which is to supply a test bay for testing machines to big for the building supply.  The generated supply will not be used/connected to the building supply.

Would the earthing arrangements be as TT with a rod at the generator connected to the neutral/star connection?


Thanks in advance ?
Parents


  • HSE leaflet  on Generators (No update ) but still relevant.


    ieeexplore.ieee.org/.../5317048


    Leaflet on Neutral inversion (No update) since 1936 (In your case original posters question  only for a read ) 

    Published in: Journal of the Institution of Electrical Engineers ( Volume: 78 , Issue: 471 , March 1936 )

    Page(s): 317 - 325

    Date of Publication: March 1936 

    DOI: 10.1049/jiee-1.1936.0051

    Publisher: IET

    ieeexplore.ieee.org/.../5317048

Reply


  • HSE leaflet  on Generators (No update ) but still relevant.


    ieeexplore.ieee.org/.../5317048


    Leaflet on Neutral inversion (No update) since 1936 (In your case original posters question  only for a read ) 

    Published in: Journal of the Institution of Electrical Engineers ( Volume: 78 , Issue: 471 , March 1936 )

    Page(s): 317 - 325

    Date of Publication: March 1936 

    DOI: 10.1049/jiee-1.1936.0051

    Publisher: IET

    ieeexplore.ieee.org/.../5317048