Ok Andy, you seem to think that total disconnection if the mains goes 20V down on normal indicates a broken CNE. It may, but may not. You can disconnect everything but disconnecting the Earth connection requires all manner of saftey systems to be safe, a single contactor doesn't do it at all. Remember that Earth connection needs to be disconnected in <40ms, just like an RCD. Any fault will disconnect and reconection cannot be automatic, can it? The fail would be all the time, not even occasionally with a real mains supply. A half-cycle at nearly zero volts is remarkably common and causes no trouble to anything except you mains disconnection idea. The problem is you do not have the time to wait, as waiting could kill someone!
Ok Andy, you seem to think that total disconnection if the mains goes 20V down on normal indicates a broken CNE. It may, but may not. You can disconnect everything but disconnecting the Earth connection requires all manner of saftey systems to be safe, a single contactor doesn't do it at all. Remember that Earth connection needs to be disconnected in <40ms, just like an RCD. Any fault will disconnect and reconection cannot be automatic, can it? The fail would be all the time, not even occasionally with a real mains supply. A half-cycle at nearly zero volts is remarkably common and causes no trouble to anything except you mains disconnection idea. The problem is you do not have the time to wait, as waiting could kill someone!