Swa cpc to motor

I’ve recently seen a motor wired directly from the local isolator to the motor terminal box in 3 core 1.5mm cable. The gland has been made off into a threaded hole in the motor terminal box and at the isolator end directly connected to the incoming swa from the MCC by means using a flylead. My question is is this a sufficient for earthing the motor. My understanding is you can use the armour as a cpc but wasn’t sure if any additional “fly leads” should be fitted at the motor end?  


thank you guys!
Parents
  • Do not ignore any potential motor vibration or physical cable impact that may loosen the mechanical connections of the s.w.a. over a period of time. A loose c.p.c. connection is not good.


    Z.
Reply
  • Do not ignore any potential motor vibration or physical cable impact that may loosen the mechanical connections of the s.w.a. over a period of time. A loose c.p.c. connection is not good.


    Z.