TNCS and earth electrode

In order to protect against neutral failures, 18th Edition states that the earth impedance between the vehicle charging earth and the true ground (or earth), for chargers fitted outside the home, must be under 200 ohms to minimise any voltage developed between the two and ensure correct operation of an RCD.
It can be possible to achieve this 200 ohms earth impedance by sinking one or more dedicated earth rods for the chargepoint. Pod Point installation guidance recommends 100 ohms as electrodes and ground conditions are subject to wide variations due to both locality and season.
Since 2013 earth rods have been required on PME systems and the flexibility that some installers used to not fit an electrode was removed from the 18th Edition in January 2019, but the difficulty of successfully fitting an earth rod predates both regulations


I am setting up an assessment for a well known accreditation body and I noted that the assessment required an installation earth electrode with a resistance of 20-200 ohms which the paperwork declared was to simulate the supplementary electrode required for TNCS systems supplying EV chargers. I contacted the body in question and a chap confirmed that was indeed the purpose of the thing. Didn't want to argue as I thought it was rubbish.  I then read the above in a technical document for the charger being used and I thought have I been drinking too much wine? Did I miss something? I am beginning to wonder. It cant be for holding down touch voltages to 70v because even at 20 ohms that would only allow 3.5A on loss of PEN. It cant be for measurement purposes as the assessment requires the "earthing conductor" to electrode to be green and yellow 16mm2. Please tell me that my daily glass of red hasnt killed so many grey cells that I have missed this?
Parents
  • gkenyon:

    The 100 Ohm value comes from somewhere though ...


    Some vehicles - the Renault Zoe is often quoted - look at the N-E loop impedance, and if it's not less than 100 Ohm, the vehicle won't charge. Don't forget, though, this is the sum of the earth electrode resistance at the installation, the Neutral run back through to the transformer, and the transformer earth electrode resistance.


    So if you've a TT installation, or you're providing a TT island for the charging point, you need to get well under 100 Ohm (preferably well under 80 Ohms) or those vehicles won't charge.


    Graham, do you know how such a test is conducted by the vehicle? Interesting that City and Guilds in their 2919 EV assessment rig require Ra to be 100 ohms.They use the TT island approach which I thought was losing favour fast for all the reasons set out in annex H of the COP. So this is another one! Not much point in providing a TT island if the car wont charge! 


Reply
  • gkenyon:

    The 100 Ohm value comes from somewhere though ...


    Some vehicles - the Renault Zoe is often quoted - look at the N-E loop impedance, and if it's not less than 100 Ohm, the vehicle won't charge. Don't forget, though, this is the sum of the earth electrode resistance at the installation, the Neutral run back through to the transformer, and the transformer earth electrode resistance.


    So if you've a TT installation, or you're providing a TT island for the charging point, you need to get well under 100 Ohm (preferably well under 80 Ohms) or those vehicles won't charge.


    Graham, do you know how such a test is conducted by the vehicle? Interesting that City and Guilds in their 2919 EV assessment rig require Ra to be 100 ohms.They use the TT island approach which I thought was losing favour fast for all the reasons set out in annex H of the COP. So this is another one! Not much point in providing a TT island if the car wont charge! 